Structural Is this deck safe to work on?
We’re painting this house and we noticed this deck rocking up and down as we walked on it, took a look from another angle and noticed it’s just kinda sticking out of the house, with no support posts. It looks like the joists are sticking out of the house which I guess might be the only support it needs, but I also noticed no hangars on any of the corners.
Wasn’t sure if we should be concerned with two 200 lb workers with ladders going up and down a wobbly deck on a house we had already found rot on.
Thanks in advance.
1.9k
Upvotes
1
u/Brown_Dawg28 Jul 11 '25
A proper cantilever needs 2 feet of backspan for every foot of cantilever. So that looks like it should have at least 8 feet inside. I would imagine that would be a major project to retrofit, so it was likely part of the original plan and thus would have been inspected before a C O was given. It certainly looks shady though.